I'm bringing an electrician in to run dedicated AC wiring from my breaker box to outlets. My powered 2 channel equipment is different from surround except for the sub (when I listen to 2.1}.  I'm look for advice from those who have done this or are electricians.

 

The current plan is 2 dedicated 20 amp circuits with 10 gauge wiring including a wired ground going back to the breaker box. There will be a grounding strip in the box, but there isn't one now. I have a grounding bar in the ground outside which is connected by a 4 gauge cable to the ComEd electricity meter. That's how my house gets its ground. I have my own  well and septic so ground is not tied to any public water pipes or my well. One breaker will be for the surround equipment and the other for 2 channel. 

 

My biggest question at this point is whether I'll have a ground loop from the sub when it's being used by the surround system. The sub will be plugged in to the 2 channel circuit. 

 

Not sure if I'm missing anything. 

Link to comment

I would have the electrician run a heavy 120V feeder (say 40 to 60 Amp) to the music room. With a small 6 breaker box in/near the room.

That way everything can be connected to the same Safety Ground in that box.

 

Let the electrician worry about the connection to Planet Earth. It's called the GEC (Grounding Electrode Conductor). What you have now is probably all you need.

Link to comment

40 or 60 amp may be overkill... But I'd run a feeder as well. I'd probably do 240V 30A (two 30A breakers) and use both "phases". When you run a sub box (2 breaker boxes) only the main box should be connected to ground, but the sub box is still bonded to ground. 

From a technical perspective, there is only ever one ground... And every thing else is bonded to it. 

I wouldn't connect your sub to both components at the same time. It's probably fine with just one running, but if you accidentally power up both, you'll be in for a surprise! 

 

Link to comment

Also, if you're using isolated ground recepticles, you must run a dedicated, insulated ground conductor back to the panel box for each recepticle. 

However, I'm unsure if these conductors have to go back to the main box or not, which wouldn't very practical.... Likely fine to the sub box. 

Link to comment

I was writing about 40 to 60 Amps for a 120V circuit or 20 to 30 Amps for a 240V circuit.

 

One of the main reasons for the breaker box in the room is so that you only need one heavy Safety Ground/Protective Earth back to the main panel.

The shorter the S.G.s are from hi-fi component to component the better.

Nothing wrong with plastic conduit or real Romex® for that matter.

And if you use plastic conduit or  Romex®, you don't need Isolated Ground receptacles.

Link to comment

The one issue that may cause some worry is that with dedicated lines, the risk of the Ground to Neutral voltage starts to climb. With mostly reactive loads in audio circuits, the voltage will increase. If the neutral to ground is more than 2V at the main panel, it will be worse at the sub panel in the music room. There's a white paper attached for further reading on elevated neutral to grond voltages.

 

One way around this, is an isolation transformer in the music room, which has the output neutral tied to ground on the secondary. The problem then is find a home for such a beast. Advantages of the transformer are common mode noise is just about gone, plus surge suppression....there's a thread on it.

 

To think further on the loss of neutral for a split 240V system would severely damage any component, therefore not recommended. A single 120V feeder would be a better option, unless of course there's protection devices that detect loss of neutral and cut off the supply for the 240V feeder.

wp202.pdf

AS Profile Equipment List        Say NO to MQA

Link to comment

yes, and his does

 

I wonder if any of the big high-end dealers there can recommend an electrician???

 

in a Metro area that large I'm sure others have done this and talked to dealers

 

or an audio club/society?

 

despite the well, you aren't really out in the sticks...

Link to comment
2 hours ago, Ralf11 said:

yes, and his does

 

I wonder if any of the big high-end dealers there can recommend an electrician???

 

in a Metro area that large I'm sure others have done this and talked to dealers

 

or an audio club/society?

 

despite the well, you aren't really out in the sticks...

 

I've asked and got a reference.  Most electricians I've spoken with claim to have experience in this area.  I've had 2 come by for quotes with one more coming this week.

 

I'm not going to spend $250/ft. on conduit.  I'd rather put the money elsewhere.  Good to know it exists though.

 

I was reading an article which stated the wiring should be "One with hot on one side of neutral.  The other on the other."  I don't know what this means exactly and it 2 electricians couldn't make sense of it.

 

Another recommendation was 4 wire cable with ground wire.  Why 4 wires plus ground?  How do the 4 wires get connected?

 

A couple other thoughts were: put power amps on their own circuit and separate heavy duty motors and compressors on a different phase from the audio equipment.

 

Link to comment
1 hour ago, Johnseye said:

A couple other thoughts were: put power amps on their own circuit and separate heavy duty motors and compressors on a different phase from the audio equipment.

Actually it would be a different leg or pole as US residential power is center tapped single phase.

Anyway, yes it's a good idea to put separate heavy duty motors and compressors on a different leg from the audio equipment.

But smaller power amps should be on the same circuit as the rest of the audio equipment.

Link to comment
1 hour ago, Johnseye said:

I was reading an article which stated the wiring should be "One with hot on one side of neutral.  The other on the other."  I don't know what this means exactly and it 2 electricians couldn't make sense of it.

Maybe it had something to do with that leg/pole thing. On leg is on one side of Neutral and  the other leg is on the other side.

So it's 240V from one Hot to the other.

On ther other hand it could mean something else.

Link to comment
4 minutes ago, KingRex said:

I'm an electrician and have done a lot of experimenting on the best way to get power from my panel to my rack.  It's easy to create a ground Loop, but it's also very easy to avoid. Grounding is a very key element in the equation. An old ground rod attached to your panel may not drain as effectively as you want it to.  Utilizing dielectric potting material or a ufer ground in your foundation will greatly reduce unwanted noise.  

While the Safety Ground connection to the Neutral is an important part of the AC power system, the connection to Planet Earth does not enter into the day-to-day operation equation. It's only there for safety during thunderstorms, high voltage failures and to keep the Neutral near the potential of the soil.

Link to comment
45 minutes ago, Speedskater said:

Maybe it had something to do with that leg/pole thing. On leg is on one side of Neutral and  the other leg is on the other side.

So it's 240V from one Hot to the other.

On ther other hand it could mean something else.

What they are saying is use the same phase.  Always A or B phase.  There can be small differences in voltage between A and B phase.  That small voltage difference can cause voltage differential to ride on the ground casing humming.  

Link to comment
40 minutes ago, Speedskater said:

While the Safety Ground connection to the Neutral is an important part of the AC power system, the connection to Planet Earth does not enter into the day-to-day operation equation. It's only there for safety during thunderstorms, high voltage failures and to keep the Neutral near the potential of the soil.

True but untrue.  It matters and will affect the SQ of your system.

Link to comment
2 hours ago, Johnseye said:

 

I'm not going to spend $250/ft. on conduit. 

 

 

 

I will bet that a stereo that can survive an electromagnetic pulse weapon is not high on your list.

 

power amps on their own circuit is good from the standpoint of power supply, but may create a ground loop...

 

how much does the Benchmark draw?

Link to comment
1 hour ago, KingRex said:

 I'm an electrician and have done a lot of experimenting on the best way to get power from my panel to my rack.  It's easy to create a ground Loop, but it's also very easy to avoid. Grounding is a very key element in the equation. An old ground rod attached to your panel may not drain as effectively as you want it to.  Utilizing dielectric potting material or a ufer ground in your foundation will greatly reduce unwanted noise. 

 

...

 

I like what you have described here - it's all about experimenting, and I've been down many paths, without actually doing something like what you have mentioned here. Once you know the quality you're after, it becomes straightforward to work out a configuration that gives something close to an ideal setup, for the equipment being used - purely via experimentation.